We are converting an existing dry system to a wet-pipe system. The entire non-conditioned area where the system was located in is being converted to fully-conditioned.
When running the new hydraulic calculations, would you keep the 100 C-Factor or would you increase it to 120 for wet pipe? For reference the dry system has been in place for approximately 30 years. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Anthony
10/7/2022 08:07:43 am
I don't believe the code speaks to this as a hard "shall" but best practice would be to use 100 c as the existing piping will have a rougher interior from the years of existence as a dry system as compared to a wet system.
Reply
Jesse
10/7/2022 08:12:29 am
C=100 would be the more conservative calc. I'd check with the AHJ and see what they want to see.
Reply
radhakrishnan duraikkannu
10/9/2022 02:15:31 am
100 C-factor shall be used, as the system is 30 years old.
Reply
Dan Wilder
10/7/2022 08:48:43 am
What does the last 5 year internal say about the condition of the pipe? Is there any indication of debris in the system (drops, low points, end of mains, top of clapper at the riser) after that long of an in-service record? Have a good look at coupling rubbers, those dry out and have caused us a lot of issues in previous conversions.
Reply
Brian Cockburn
10/7/2022 09:23:49 am
I tend to think using C=100 would be the better choice as the pipe interior would be rougher, as mentioned above. That being said, scoping the inside of the pipe would tell you what condition it's in and you can use that to inform your decision.
Reply
Glenn Berger
10/7/2022 09:53:46 am
I agree with Dan's comment above. My question is how much of the existing system is being changed out? Are you just swapping out the control valve or something more invasive?
Reply
10/7/2022 10:06:14 am
I would definitely do an extensive internal pipe check and a thorough 5 year prior to doing anything to a dry system that has been in place for 30+ years.
Reply
Alex
10/7/2022 10:47:34 am
Hi,
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |