Do underground gate valves for fire main water supplies have to be monitored and supervised?
Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments
Randy
1/20/2020 09:33:37 am
Not necessarily. See NFPA 24-2019 Section 6.7.2
Reply
Franck
1/20/2020 11:48:09 am
But many AHJs request it for private facilities, in particular Insurance Companies.
Reply
Jim Abernathy
5/20/2021 10:00:38 am
I have four underground 8 inch valves with valve boxes. How do I supervise these valves?
Reply
Joe Meyer
5/20/2021 10:05:32 am
Usually two options - chain and lock the valves, or run tamper switches from fire alarm out to the valves for electronic supervision. The requirements very much depend on the enforceable local codes.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |