For areas with high water vapor concentrations (such as near showers, steam rooms, etc), what type of sprinkler would perform best? Wax coated? Concealed with gaskets?
There's many circulated images of corroded sprinklers, but I'm interested in what others feel is current best practice for these areas. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
8 Comments
Colin Lusher
12/4/2019 10:11:08 am
I work in Hawaii where corrosion is a huge problem due to the salt air....we've had the BEST luck with the Electroless Nickel PTFE (ENT) coated sprinklers (by Viking, Reliable, or Minimax). They hold up much better than poly coated sprinklers for corrosive environments, and look better than wax coated sprinklers.
Reply
Hector Ramirez
12/4/2019 10:23:57 am
It's my understanding that you would use polyester finished sprinkler heads in such indoor corrosive conditions, and ENT for outdoor corrosive conditions. Feel free to correct me, I'm still relatively new to the industry.
Reply
12/4/2019 01:53:44 pm
Hector,
Reply
12/4/2019 12:49:03 pm
There are Stainless steel sprinkler nozzle introduced on the market coming from Reliable and Viking. Material is SS316 which will greatly provide protection from corrosive environment.
Reply
12/4/2019 01:58:15 pm
Yes, I believe most sprinkler brands carry stainless steel option, however they are often cost prohibitive. I recently priced them at nearly $200.00 per sprinkler. These are typically only necessary in highly corrosive environments, often chemically corrosive industrial applications. For a standard corrosive environment due to humidity, poly or ENT coated heads are fine, and at a fraction of the cost ($10-$30 per head).
Reply
Jonathan Hatcher
12/4/2019 04:32:47 pm
For corrosion resistance, stainless steel sprinkler heads are hands down the best option. However, they come with a hefty price tag. Depending on the type of environment, the ENT coated heads perform well for corrosion resistance. Be careful using ENT coated sprinklers in chlorine rich environments as I've had experience with them degrading rapidly in that type of installation.
Reply
Chris Covalt
12/5/2019 08:08:49 am
There are coatings available from the manufactures. Victaulic has a VC-250 coating we are using on a parking garage. Tyco, Viking and others also have their own coatings. The manufacture should provide a salt-spray test report on their coating giving you an idea how the coating will perform. SS heads are the best but they are 5 times the cost. Special coatings, such as the VC-250 are next best.
Reply
Kevin Sneed
1/9/2020 09:55:42 am
Would the use of chlorinated polyvinyl chloride (CPVC) pipe a viable option versus cooper piping for sprinkler system?
Reply