Can two electrical boxes be placed in the same stud cavity?
If so, are there restrictions by code? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Adam
8/19/2022 08:26:20 am
I'm assuming this is in a fire-rated wall, and the boxes are on opposite sides of the wall within the same stud cavity.
Reply
David Toshio Williams
8/19/2022 04:08:59 pm
Better to have them in separate stud cavities, but even there you have to be sure the studs create the proper fire separation. The wall assembly as identified in the UL (or other) listing should help you with the required separation.
Reply
sean
8/20/2022 06:39:52 am
If in a rated wall in the same cavity you can use a rated fire stopping system (putty pads) to restore the rating.
Reply
Jim Sills
5/3/2024 08:25:06 am
https://code-authorities.ul.com/wp-content/uploads/2014/04/Ul_outletboxes.pdf
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |