I am currently working on an existing high rise building that requires a fully automatic sprinkler system to be added and the AHJ is requiring a water tank to be added on the property to serve as a secondary supply.
There is no room for a secondary supply. Can a pool be used to substitute a water storage tank that will supply the building through fire pumps? What codes could back up this option? Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
24 Comments
1/28/2021 09:25:19 am
As stated in Fire protection Handbook, The developed sources of water supplies adapted for fire fighting are limited only by the innovation of the fire department. Developed sources include cisterns, swimming pools, quarries, mines, automatic sprinkler system supplies, stationary tanks, driven wells, and dry hydrants.
Reply
Glenn Berger
1/28/2021 09:27:44 am
Using a swimming pool as a water supply is a consideration that I had never thought to use. Need to have an understanding of chemicals being used in the swimming pool and its potential effects on sprinkler piping. I am sure others will be contributing and curious on their opinions.
Reply
sean
1/29/2021 07:00:24 am
I think the concern is not about not how the agents affect firefighting but that the water can be drawn without injury if someone was in the pool.
Reply
Aaron McWilliams
2/28/2024 11:38:15 am
In a standard swimming pool the chlorine content is 1 to 3 ppm of chlorine. Up to 2ppm of chlorine is suitable for drinking water. With the exception of salt pools the other levels in the pool ie PH, Alkalinity, and Hardness should all be kept within no corrosive levels. I don’t know why even large pools are not used as storage sites for fire fighting.
Reply
Thomas Jones III
1/28/2021 09:28:04 am
You may want to look into NFPA 1142. I have personally never designed a system like this but I have seen it done before.
Reply
Josh Gilliam
1/28/2021 09:32:50 am
I would say be mindful of the fact that there are times that pools are drained for maintenance and whatnot. If the pool is enclosed, that would be more helpful than say a rooftop pool for obvious reasons. If you find code and present to the AHJ, I'd like to know what you find out.
Reply
HJ
1/28/2021 09:50:49 am
One AHJ's 2 cents,
Reply
HJ
1/28/2021 09:55:47 am
PS: While I would not let the pool be connected to the fire pump at all, the AHJ may allow you to install a draft FDC on the pool per NFPA 1142, as an auxiliary water supply option only.
Reply
James
1/28/2021 09:57:50 am
My guess is, though, this isn't an NFPA 1142 application since a high-rise would typically be in a dense urban area. Don't know the OP intent, but I don't think 1142 would get pulled in.
James
1/28/2021 09:58:19 am
To your point on rural applications, yes and I agree that's a pretty sound approach.
HJ
1/28/2021 02:36:49 pm
NFPA 1142 contains the guidelines for draft/dry hydrants. The AHJ in the posted scenario should be able to determine whether they can/should apply it, sounds like they are...creative. =)
Samuel C Harbert
5/2/2022 11:47:32 am
Hello, I was wondering if you could provide some more details or docs on this. We are working with a rural project and the North Dakota State FM and they are open to the idea but would like to see examples of where this has been done before.
Reply
Chris Geer
1/28/2021 09:57:00 am
Years ago I recall someone mentioning that if the sprinkler system activated, and a fire pump was involved, anyone who may be in the pool at the time of activation would be sucked into the suction piping...
Reply
Bruce Seiler
1/28/2021 09:57:36 am
We have installed a system utilizing a pool as a primary and secondary supply. The concern is always will the pool be full at all times or will it be drained and unused. Pre-cautions should also be put in place that when the pool is drained, the system is considered impaired. Time frames for filling should be considered the same as a tank. There was project that utilized a pool for the supply and near the end of the project there was a fire which burned the entire building. The sprinkler was installed and complete, however the pool had not been filled.
Reply
CJ Bonczyk
1/28/2021 10:30:28 am
NFPA requires that the sprinkler system must have one automatic water supply. NFPA does not prohibit its use as a means of a water supply if the pool is sufficient in size to meet the demand of the most demanding system (i.e. standpipe or sprinkler) and meets greater of the two duration requirements. A pool is similar in design to a UG water basin being the supply which would be pumped by a vertical shaft turbine pump or similar.
Reply
Brian R, VCook
2/28/2021 06:52:52 pm
Well Said!!
Reply
Pari
1/28/2021 10:46:55 am
Instead of pool you have an option to use Section 914.3.1.2 of IFC: Fire pump can be supplied from two water main located in different streets. if project located in corner lot and can be supply from two different main.
Reply
Marc Vieno
1/28/2021 11:36:06 am
This is the solution that most new high-rises in Portland use.
Reply
Dave L.
1/28/2021 10:48:20 am
I addition to the concerns above, the pool's ability (or inability) to withstand a seismic event.
Reply
Tati Naga Sai Chandu
1/29/2021 01:28:10 am
As per the NBC-2016 section 7 classification of buildings it has mentioned based on the type of building what storage, How much of water required. But i am sure you need to convert it as a dedicated water sours with standers water storage capacity based on the NBC-2016 or NFPA. Automatic sprinkler system supplies, stationary tanks, driven wells, and dry hydrants.
Reply
5/5/2021 03:47:42 pm
This is a system which uses the swilling pool as the water source and covers a 250 foot circle with a two story home.
Reply
12/27/2021 02:57:03 am
With the cover protecting your pool, it is less likely for chemical imbalances to occur. Thus the pool chemicals needed to maintain your pool all year round is less likely to be unbalanced. Nonetheless, always monitor your pools pH level to ensure they are optimal.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |