According to the International Building Code Section 905.3 (2018 Edition), a standpipe is required in any building with four or more stories.
We have a small building (three family homes) but the first floor is all a parking garage, and then 3 more floors over the parking garage (one home per floor). According to the IBC, do we still need a standpipe even if it's such a small building? If we do need a standpipe, does the service have to be 4-inches or can we have it at 2-inches and increase the riser up to 4-inches to feed the manual wet standpipe? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Alex
6/6/2022 07:04:10 am
Hi,
Reply
Pete H
6/6/2022 07:37:26 am
I'm inclined to agree with Alex, you need the standpipe (you got four stories). And to continue to agree, you can probably get away with the 2" service that increases to 4" at the riser (so after the backflow) provided you can make the mandatory calculations work.
Reply
Anthony
6/6/2022 08:56:27 am
No calculations required, It would be a manual standpipe system, assuming there is a sprinkler system. The 2'' backflow it a sprinkler problem, not a standpipe problem.
Reply
Alex
6/6/2022 01:19:07 pm
Anthony,
Todd E Wyatt
6/6/2022 08:49:05 am
The first step in evaluating fire protection requirements is to identify the Occupancy Classifications (OC) of the building. You state that the building includes "three family homes" which could be classified as Group R-2 Residential. (Standpipes are not required in R-3 occupancies).
Reply
M. Newell
6/6/2022 08:49:23 am
I think it largely depends on the occupancy above your parking garage.
Reply
Dan Wilder
6/6/2022 08:58:56 am
Points of clarification:
Reply
Todd E Wyatt
6/6/2022 10:01:02 am
2021 IBC
Reply
Dan Wilder
6/6/2022 11:04:40 am
My request was not to remove the standpipe requirement but identify if a 13R system is even the correct application. If the building goes to a full 13 due to the height of the building, a 2" domestic water feed isn't going to cut it.
Ed Kramer
6/6/2022 11:33:07 am
Designed a project a few years ago that required a manual wet Class I standpipe. The standpipe system (from the most remote hose valve to the FDC) was sized via hydraulically calculations. Most of the standpipe system was 4" with some of the common supply pipe near the FDC as 6". I don't recall the reasoning, but we chose to run a separate vertical supply for the sprinkler system, so the standpipe was standpipe only - not a combined system. To make the standpipe 'wet', we connected it to the sprinkler system riser using 1" pipe.
Reply
Jesse
6/6/2022 02:44:11 pm
Its not stories, per se. But rather vertical distance of the occupiable floors above lowest level of fire apparatus access. I actually have a 4 story hotel right now with the 4th floor 28-6 above the fire lane so it has no standpipe. Likewise, I had a 3 sto prior that did.
Reply
Menachem D
9/4/2023 02:36:32 pm
I am working on an R-2 multi-family house three stories + underground basement + Attic.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |