Does any one know in 1960's and 1970's, what the flow and pressure requirements of 1-1/2 inch standpipe system hose of NFPA 14?
This would be for a Class II system. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Dan Wilder
5/9/2024 08:08:53 am
This was the proposed changes to the 1968 version. If you don't get an answer here, call NFPA and ask them as they can provide the info. The Sprinkler Academy (Cecil Bilbo & Mark Karr) also have a great archive that you could reach out to.
Reply
5/9/2024 08:18:52 am
100 gpm at 65 psi residual pressure . In 1993 it increased to 100 psi
Reply
Jack
5/9/2024 09:52:48 am
Agree. This was for standpipes not hose stations.
Reply
Brian Cockburn
5/9/2024 10:13:40 am
I don't know if this would be helpful but SFPE has a free webinar on Standpipes that covers pre and post-1993 requirements.
Reply
Jesse
5/9/2024 11:37:54 am
65 psi!
Reply
OP
5/9/2024 11:44:08 am
Many thanks to every one for providing answers and references!
Reply
Jerry Clark
5/10/2024 08:54:27 am
The flow requirement for a 1-1/2 inch standpipe hose was generally in the range of 50 to 100 gpm. The pressure requirement typically ranged from 50 to 100 psi. Specific requirements may have varied depending on the edition of NFPA 14 in effect. Additionally, local building codes and regulations could have imposed specific standards or modifications to these requirements based on regional considerations and fire safety needs.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |