I have 30-inch deep beams which are spaced just under 5'-0" apart running east to west.
I have 48-inch deep beams running north and south spaced 24'-0" apart. Do I have to get a row of sprinklers in every 5-foot pocket? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Anthony
7/22/2022 07:15:42 am
Yes you do need to be in every pocket.
Reply
Alex
7/22/2022 08:52:42 am
Hi,
Reply
Dan Wilder
7/22/2022 08:39:08 am
Not knowing what the hazard classification is or the bottom flange width...
Reply
Barry
7/22/2022 09:13:09 am
If these are concrete beams, Is it possible the beams actually meet the NFPA 13 Definition of concrete tee construction?
Reply
Jesse
7/22/2022 09:27:51 am
Would love to know a little more. Wooden beams? Concrete?
Reply
danefre
7/22/2022 10:20:46 am
A lot of variables here...
Reply
Mickey Rowe
12/27/2022 12:27:39 pm
I have obstructed solid 18" steel beams with pockets being over 320 sq foot. The area is OH Grp 2 warehouse. Can I space my lines 14 ft apart if protecting every pocket.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |