We have a project with telescoping wooden bleachers.
Are sprinklers required to be installed underneath these? If so, how is that done properly? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Todd E Wyatt
11/24/2022 08:39:30 am
It depends on the adopted (scoping) Code (e.g. IBC, IFC, NFPA 101 …) and the Occupancy Classification(s) (OC) of the building (or portion of the building) with the bleachers.
Reply
11/28/2022 04:36:04 pm
Todd,
Reply
Glenn Berger
11/24/2022 09:00:39 am
Todd gave you the precise code requirement.
Reply
Alex
11/24/2022 10:30:54 am
I found the following letter from Louisiana Building Department for further interpretation. I believe Todd captured the complete response though.
Reply
11/28/2022 04:42:31 pm
Thank you for the reference. At least Louisiana is giving more concrete direction.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |