I'm designing a school that has overhead doors that are 8'-0" x 7'-0" that run up above a 10'-0" or 10'-6" ceiling. The structure is non-combustible (steel beam & steel bar joist) and the walls go deck.
The opening for the door in the drop tile ceiling is an 8'-6" x 1'-0" opening. This opening does not meet the 70% open ceiling requirement and I'm not sure it meets cloud ceiling requirements. The plan reviewer is asking me to place upright sprinkler heads above the ceiling. My interpretation is that I don't need sprinklers above the ceiling. Are sprinklers required above the ceiling? Thank you in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Alex
8/26/2021 07:58:24 am
Hi Anonymous,
Reply
Alex
8/26/2021 08:11:26 am
HI quick follow up, Joe also wrote a good post on this a while back (3/7/2018). If you click on Blog and search 'A New Calculator for Cloud Ceiling Sprinklers' you will be able to see his explanation of the code.
Reply
Franck
8/26/2021 08:24:10 am
Is the door combustible ?
Reply
Steven
8/26/2021 08:41:19 am
If I am understanding it correctly, the door slides straight up (along straight tracks) into the 8'-6" x 1'-0" opening, and the concern is that there is an opening in the dropped ceiling to the space above.
Reply
Glenn Berger
8/26/2021 09:12:20 am
I have additional questions -
Reply
Pete
8/26/2021 01:58:41 pm
I have to agree with the posters who asked the question about the combustibility of the door, and would also extend it to the general school construction/structural members in the area.
Reply
Mike
8/31/2021 08:12:44 am
I did a firehouse addition, occupied 24/7, where sprinkler heads were required above and below doors because the roll up doors were left open for extended periods of time. They were viewed as an obstruction over 48" wide.
Reply
Tim
3/15/2023 09:36:51 am
I have this same situation and am curious how this was resolved. Protecting 24' around the gap seems excessive. I have a 13' x 10" gap, putting it outside of the 8" gap allowed for lengths over 4' into a concealed space. If cloud ceilings with a 10' CH allow a 10" gap (with under 150 sq. ft. spacing per NFPA 13-2016 Table 8.15.24.1) why would this single gap in a 406 sq. ft. room require it?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |