I have a project with a workshop space that has a ceiling height of 70-feet from floor level.
How do I approach sprinkler selection & system type for this height? Does NFPA 13 have a ceiling height limitation? I see a couple of tables in FM Data Sheets, but is this the only source for protection at these heights? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Alex
8/9/2022 06:31:15 am
Hi,
Reply
Hi,
Reply
Casey Milhorn
8/9/2022 08:35:52 am
I don't recall any limits on ceiling heights for non-storage applications. There are some limitations when dealing with cloud ceiling protection, reduced area, and then also some exclusions for atrium protection (if I remember correctly). I have installed sprinklers in an 80' tall building before and I've seen 100'+ (non-storage) areas with roof level sprinklers.
Reply
Anthony
8/9/2022 08:45:38 am
There are no NFPA 13 height maximums, however I'd consider spacing the heads tighter 100 sqft max and a larger K factor 11.2 or 14
Reply
Glenn Berger
8/9/2022 08:50:19 am
With ceiling heights at this level, I would recommend a fire modeling exercise be undertaken to determine an useable design criteria. Based upon other projects that required a significant clear height, a deluge system was required. We installed several "draft curtains" to limit the size of each system, which cut down the required water flow.
Reply
Chris Nelson
8/9/2022 09:33:02 am
If you can consider it an atrium, atriums over 55ft from ceiling to floor don't required sprinklers. Was looking into this morning for industrial buildings where they combine pieces of ships.
Reply
Franck
8/9/2022 12:36:57 pm
No height limitation for occupancy hazard.
Reply
Dwight H Havens
8/10/2022 08:14:05 am
I go with Glen Berger's comment. What is the minimum fire load necessary to actuate a fire sprinkler at just under 70 feet of height?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |