I have a project for a Cast and Forging plant, which requires a "double interlock sprinkler system per NFPA 13". That's the first I've heard of a "double interlock sprinkler system".
My question is do I have to use a deluge valve or would this be an alarm check valve? Would nozzles be open or closed? Many questions, thanks. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Alex
9/22/2021 06:52:23 am
Hi Anonymous,
Reply
Jesse
9/22/2021 08:25:12 am
Not sure what you're referring to as "nozzles". I'll presume your mean sprinkles. Sprinklers are closed as part of the double interlock requires a sprinkler fusing.
Reply
Jesse
9/22/2021 08:59:17 am
To clarify, valve should be electric / electric or electric / pneumatic
Reply
Kell
9/22/2021 08:38:37 am
Double Interlock would be something like the Tyco DV-5 valve with the required trim, be it Electric/Electric or Electric/Pneumatic which ever detection type is required (Preaction System). The sprinklers would be regular wet system sprinklers, NOT open Deluge type or Nozzles.
Reply
Glenn Berger
9/22/2021 09:12:46 am
The above responses all assume that the requirement is for a "Double-Interlocked Preaction Sprinkler System. You can have a "Double-Interlocked Deluge System. Submit and RFI to get this clarified. The RFI should also include the means of actuating the system.
Reply
Alex
9/22/2021 09:54:01 am
Good point, Glenn. My mind didn’t even cross that road.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |