We have a project light hazard occupancy, that is a highrise building, and has glass all along the perimeter of the building.
Is the maximum sprinkler spacing measured off the knee wall, or the glass? There is a knee wall that rises up from the floor 2'-6" and is 12-inches in depth. Do we measure the 7'-6" off this knee wall for floor coverage, or do we measure off the glass for the maximum distance? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Mike L
1/12/2022 07:25:53 am
We typically measure the spacing off the face of the glass. The thought being the top of the kneewall will be covered with people's effects (aka combustible load).
Reply
Alex
1/12/2022 08:05:22 am
NFPA 13 (2016) 8.5.3.2.4 states that sprinklers shall be measured to the wall when sprinklers are spaced near windows and no additional floor space is created.
Reply
Jesse
1/12/2022 08:18:42 am
Typically, the measurement would be from the face of the wall. However, in your case it should be from the face of the glass. This will inevitably become a shelf or something.
Reply
SCHULMAN
1/12/2022 08:44:10 am
ok, I'll dissent ...
Reply
Dan Wilder
1/12/2022 09:02:04 am
This is where a conversation with the AHJ is good to have and followed up with for documentation. The knee wall is likely hiding the floor/window interface & rating (the framing holding the exterior glazing to the building along with the smoke/fire horizontal assembly). This isn't floor area by definition and the recessed window area should not be counted/defined for sprinkler spacing (the NFPA handbook has a section view illustration).
Reply
Casey Milhorn
1/12/2022 09:09:02 am
I would have to agree with Schulman on this one as well. Sometimes it feels like we are getting too legalistic with interpretation in todays time. I would argue the load is going to be very light, the spray pattern of the head (tested to a flat wall in fire tests) will get some additional throw due to the elevated knee wall. Additionally the surface beyond and underneath the fire load is non-combustible. I agree with a discussion with the AHJ is the best approach though.
Reply
Jack G
1/12/2022 10:11:36 am
In a high rise building it is always good practice to space off the face of the glass.
Reply
Anthony
1/12/2022 04:34:04 pm
Some questions to consider:
Reply
Jonathan Joseph
1/12/2022 04:56:21 pm
9.5.3.2.3 (2019) The distance from the wall to the sprinkler shall be measured to the wall when sprinklers are spaced near windows and no additional floor space is created.
Reply
Dwight H Havens
1/13/2022 05:43:33 am
As previously noted the NFPA 13 standard indicates that the spacing is to be measured to the wall, not the glass. I think that it is also important to remember that the spray pattern from a standard spray pendant or upright sprinkler is circular, not a box, extending out to 11.25 feet, so unless the window sill is more than 3.75 feet, it is expected to be within the design coverage of the sprinkler. Such a deep window may require special consideration.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |