We have a project with a generator room on the outside of a building. There is a large louvre to an air chamber that is about 8-feet wide before another concrete wall is to be erected. The concrete wall has some bracing back to the main building.
Is there a reason sprinklers should be required in this air chamber that is open to the sky? I'm looking for code help either way. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Mike
7/8/2021 08:16:05 am
If it's open to the sky, how will you get the heat to accumulate and then actuate the sprinkler?
Reply
Dan Wilder
7/8/2021 09:00:45 am
This sounds no different than a make up air shaft we see on enclosed or underground parking garages with the metal grating at the top to prevent people from falling in (if there is even that much protection at the top).
Reply
Todd Wyatt
7/8/2021 09:18:20 am
The applicable Building Code (e.g. 2021 IBC) will determine where an "approved automatic sprinkler system" (AASS) is required and where it is exempt from being installed. The referenced standards (e.g. NFPA 13) includes the "hows" for the design, installation, testing, and maintenance for AASS, but not necessary the "where."