There are restoration companies like Servpro that store furniture in large boxes in warehouses (some are wood and some are metal) for restoration. I have been told that the boxes are considered temporary since the items are restored and then moved back into the facility where it came from, but they can still be in the warehouse for months packed with all types of furniture.
NFPA 13, 2016 Table A.5.6 specifically lists "Storage container- Large container storage of household goods" as an example of a commodity that is not addressed by NFPA 13. I'm not intentionally picking on servpro because there are other companies like this, but servpro happens to be a popular one in my area so this is the example being used. See an example of wooden storage boxes in the warehouse here: https://www.youtube.com/watch?v=OiyPxTr2Tgg 1) Has anyone else protected an occupancy similar to this and can provide some insight? Do the boxes need to have sprinklers dropped in them while they are in the warehouse? 2) If this situation does fall into the "Large storage containers" not addressed by NFPA 13, does anyone know what standard I can utilize to adequately protect this space? I appreciate any feedback. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
sean
5/1/2020 11:15:00 am
you would not put sprinkler inside the wood boxes.
Reply
Noah Koski
5/1/2020 11:52:33 am
I sent this situation NFSA's "Expert of the day" service for their opinion and their unofficial interpretation is that this does fall into Table A.5.6 for examples of commodities that are not addressed by NFPA 13. The recommended solution in this situation would be to consult a Fire Protection Engineer for guidance to come up with a protection criteria that is acceptable to the AHJ since it is not addressed by any NFPA or FM Global standards at this time. Apparently this was discussed with PODs storage and there were plans of doing large scale testing of large storage containers stacked up to four units high in 2018, but I haven't been able to find anyone about it.
Reply
sean
5/1/2020 03:58:49 pm
I am looking at what I would expect to see in the wood crate. That would be some form of group A plastics (between modern furniture, and we have in our houses today). Glancing at NFPA 13 2016 table A.5.6.1.1 under group a plastics they have examples of just plastics or mixed materials. If people are storing furniture and house hold goods you would expect it to be a mix, but you never know so I would assume someone is storing a full container of cushions or all plastic parts,etc. The next column specifically calls out wooden crates. This differs from PODs they use a metal container and why testing would be warrented. So half way down you get the following:
Reply
Mike
5/1/2020 12:43:07 pm
Go for the worst case. No one can fault you for that.
Reply
Franck
5/4/2020 04:53:04 am
By looking on the youtube video you provided, I don't think that your commodity falls into the "large storage containers" (just like the one you send overseas on large boats), but is indeed "stuff stored inside wooden boxes".
Reply
Noah Koski
5/4/2020 06:03:57 am
I found a great article on the SFPE page that covers this topic really well.
Reply
The business owners and realtors, clearance defines how high they will physically store. Clearances are typically are considered the space from the ground to bottom of roof structures like trusses, etc. To the hearth departments and code users, clearances are short for usually termed to explain the space between the highest of the storage to the sprinkler deflector.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |