We have a client that is looking at building a fireworks retail store on the edge of town. The county is requiring the store to be sprinklered, but no one can give any direction on how to protect it and NFPA does not call out coverage for this type of business.
It is an H-3 occupancy, covering roughly 10,000 sqft. Is there a standard that offers guidance on how to go about protecting a facility like this? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Glenn Berger
4/16/2021 08:07:24 am
You will not be able to protect the facility if the fireworks are ignited.
Reply
Craig Hanson
4/16/2021 08:12:52 am
Type 1.4G fireworks are covered under NFPA 1124, CPSC 16 CFR parts 1500 and 1507. Also you can look at the IFC chapter 56 for other information that will mostly mirror the above regulations
Reply
Mark A Sornsin
1/3/2024 08:42:19 am
As of today, NFPA dos not have a prescriptive solution for the protection of retail fireworks. NFPA 1124 has not provided a prescriptive solution since the 2006 edition, after which it was intentionally removed.
Reply
Jesse
4/16/2021 08:33:59 am
That's outside the scope of NFPA 13. Look to NFPA 1124 for storage requirements.
Reply
matt
4/16/2021 08:34:25 am
check out NFPA.org
Reply
CJ Bonczyk
4/16/2021 08:51:56 am
Be advised currently NFPA 13 does not have a definitive protection criteria. Both NFSA and AFSA recommend a Fire Protection Engineer should be consulted and hired to determine the protection criterion on a case by case basis. NFPA 1124 Code for the Manufacture, Transportation, Storage, and Retail Sales of Fireworks and Pyrotechnic will provide some guidance. Also IFC Chapter 56 covers Pyrotechnics. If any of the fireworks are a Division 1.3G, they are categorized with explosives in the IFC and it requires storage to be in magazines.
Reply
chad
4/16/2021 11:10:19 am
NH requires retail fireworks shops to be sprinklered. It will stop small fires in them as long as it doesnt involve a mass amount of the products:
Reply
chad
4/16/2021 11:17:38 am
By the way that facebook post eludes to an "high hazard" system. I assume this refers to EH2 design curve or something like that.
Reply
Tony
5/4/2021 01:31:21 pm
I am assuming you are under the IFC, if you are under NFPA 1/101 check NFPA 400.