We have a new construction building that's wood frame (Type III-B), and we have an 8-inch horizontal standpipe. It's hung from wooden trapeze (two 2x4's) spanning wood floor trusses. Per NFPA 13-2019 Section 17.1.7.1, hangers and their components shall be ferrous metal.
Is a ferrous metal trapeze (steel angle or pipe span) permitted to span wood floor trusses? If so, must the trapeze avoid attaching to the web components of the truss? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Anthony
2/2/2024 07:20:51 am
First off obvious answer that'll to just hang of that I beam in that photo and move on.
Reply
Dan Wilder
2/2/2024 07:39:57 am
The AWC provides section modulus values for sawn lumber but it's based on a distributed load not single point (that I can find readily). Unfortunately, not only did they use a 2x in the worst orientation, even if it is doubled up, with shorter spans, and it looks like they did a through connection with washers & nuts, this really needs to be signed off by the truss structural engineer and the building structural engineer.
Reply
Jesse
2/2/2024 08:15:52 am
I'd love to know more about why they ran dimensional lumber that way...
Reply
Mike F
2/2/2024 08:17:44 am
Dan W. Is right on with the answer. Question with the steel I Beam so close, why did they not hang right from the steel shown in the picture
Reply
Chad
2/2/2024 08:18:56 am
100% argree.. you need a PE ok that added load to an engineered truss, there is no truss manufacturer that ok’s significant loads like that on their spec sheets…. Especially to the bottom chord.
Reply
Josh
2/2/2024 08:59:58 am
The ultimate irony of the decision is the beam not only appearing in the same picture, but being right next to it.
Reply
DAN
2/2/2024 09:34:52 am
Plus- the traps should be supported from the top cord pf the truss...not the bottom
Reply
Rlujan
2/2/2024 09:42:58 am
My guess is they offset from the beam to allow the pipe, which looks to be six in., to pass the column without adding extra fittings.
Reply
Jack G
2/2/2024 09:53:24 am
#1- are the floor joists rated for mechanical load.
Reply
Dave
2/2/2024 10:43:11 am
There’s some relevant commentary in the NFPA #13 handbook, but it basically says, “where materials other than steel are proposed for trapeze members, an engineering analysis must be completed to determine the material’s capability.” You can’t go by gut-feel; the building designer has the option to modify the structure. As Jack says, consult the truss manufacturer’s guidelines and details (in our neck of the woods it is usually Red-Built / old TJI). If suspending the top chord, remember one must have enough meat below the attachment point, plus per NFPA 13 each individual component of the trap must be sized for the 8-in. pipe being supported.
Reply
Pete H
2/2/2024 01:09:25 pm
The beam is right there. Put a beam clamp on the rod and stop hanging from the wood trapeze.
Reply
sean
2/4/2024 09:28:03 am
this photo is so wrong. hanging from the bottom of a truss/joist shouldn't be done unless prescribed by the engineer.
Reply
2/7/2024 02:40:02 pm
The ferrous hanger components (Listed pipe clamp and ferrous threaded rod meet NFPA 13 requirements. The wooden beam needs to be calculated and certified by a Registered Professional Engineer.
Reply
Chris
2/8/2024 08:58:22 am
You are allowed to hang from wood structure but technically it is only considered wood structure if the framers were the ones that put it there IIRC, you are not to add wood yourself to hang from. If you cant hang off the H beam in the photo I would say you will need to install a steel member for the trapeze to the top cord of the truss, a piece of angle iron or unistrut may be easiest.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |