For low-pile/miscellaneous storage, NFPA 13 has Group A protection up to 5-ft in height requires Ordinary Hazard Group 2 criteria. It also requires Class IV up to 12-ft as Extra Hazard Group 1.
Could you, theoretically, design for Extra Hazard Group I, but put the Group A in the 7-12ft range with Class IV below? There would be no commodities above the Group A plastics, but I'm not sure that the Class IV would be protected throughout properly. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
2/4/2022 07:15:41 am
I'd be leaning on no. I think the added elevation of the group a plastics would put you in EH2.
Reply
Chris Nelson
2/4/2022 08:24:12 am
This is actually my question. Thank you for your response Pete! I see where you would call out the EH2, but that would only be applicable for miscellaneous storage as only 5ft is allowed in "low piled storage" in accordance with NFPA 13 13.1.1(6) which is where my question is really trying to answer. The handbook does point to that fire characteristic take on those of the higher commodity but thats where it get me with the OH2 vs EH1. In any scenario we expect the Group A to become involved rather quickly, but my thought was that the EH1 would quickly extinguish the Group A as we have 0.3 vs 0.2 gpm/sf and then handle the Class IV throughout as required in the table though extinguishment time would be expected to be lengthened.
Reply
Pete H
2/4/2022 09:05:41 am
Good pick up on 13.1.1(6).
NK
2/4/2022 08:17:37 am
This is addressed in NFPA 13, 2016 chapter 5 section 5.6.1.2.3. The handbook (page 107) has a research note that talks about this also
Reply
Chris Nelson
2/4/2022 08:28:07 am
Mixed commodity 5.6.1.2.3 is actually the path that I took for my project as it was the most conservative. But since the Group A only requires OH2 but is only up to 5ft and the EH1 is for Class IV up to 12ft. My question is more for is "up to 5ft" allowed in any point in space and if its allowed to be applied when storage above other commodities.
Reply
Franck
2/4/2022 08:54:32 am
If you put Group A commodity with Class IV (imagine Group A from ground to 5 ft and class IV above), it may ends up that all is to be considered as a Group A commodity.
Reply
Chris Nelson
2/4/2022 09:49:26 am
I completely agree and my company generally "baby this client" to prevent them from forgetting how we need them to store things, which is why I went with the mixed commodity allowance of chapter 5. The whole "don't put group A next to each other" is easier to police than my thought process of keeping group A only in the7-12ft range of a rack.
Reply
Franck
2/4/2022 03:10:37 pm
If you have class IV from 0 to 7 ft and then group A from 7 to 12, it would be worse than class IV from 0 to 12 and EH gr 1 is not sufficient.
Jesse
2/4/2022 09:01:09 am
No. We protect the "overall" commodity class, not just the most prevalent commodity class. The 2016 version of 13 kind of changed how we determine that.
Reply
Shaunna
2/4/2022 10:46:04 am
13.1.1 calls out and separates Miscellaneous storage of Group A plastics up to 12' in height.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |