I'm designing the fire suppression system for a 6-story wood frame residential building. There will be 6-ft wide balconies made of non- and limited-combustible materials. Normally that would mean sprinklers under the balconies could be omitted, but it occurred to me that people will likely have BBQs and the accompanying propane tank on their balconies.
Would this count as "combustible storage" and thus require sprinklers (dry sidewall heads), or can they still be omitted? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
16 Comments
Peter Howard
5/6/2021 06:43:46 am
My "hot take" would be that the bbqs likely aren't "fixed" equipment, the propane tanks certainly aren't, and any of the storage defined could probably be considered transient or miscellaneous due to the portability or size anyway.
Reply
Richard Koenig
5/6/2021 08:14:57 am
I agree with the comments above and ran into a similar situation for a High Rise project several years ago. The AHJ did require dry heads cover the balcony for the reasons above and stated that some tenants my add an enclosure which would change the status from an open balcony to an enclosed room.
Reply
Mike
5/6/2021 08:15:07 am
Apartment complexes typically ban any kind of cooking/grilling on the balcony.
Reply
Joshua Freedman
5/6/2021 12:40:10 pm
NFPA 1 specifically prohibits use or storage of hibachi, grill, or other similar cooking devices on any balcony, under any overhanging portion, or within 10 ft of a structure. However, many AHJs will allow exceptions for fire resistive, sprinklered structures.
Reply
Michael Schulman
5/6/2021 08:17:43 am
How are the balconies "made of non- and limited-combustible materials" when it's a wood-framed building ?
Reply
Brian Cockburn
5/6/2021 11:08:08 am
I should have specified - the balconies are wood frame but the undersides either have metal soffits or fire rated sheathing. They are 1 hr fire rated assemblies.
Reply
MICHAEL SCHULMAN
5/6/2021 11:17:20 am
Well, my opinions come from the engineering and design side which it sounds like you are in ....
DS
5/6/2021 08:26:01 am
If the jurisdiction follows NFPA 1:10.10.6, the grills and propane tanks could not be used or stored on the balconies.
Reply
Steve
5/6/2021 09:18:03 am
I agree with the above. NFPA 1 specifically proscribes grills and BBQs from balconies. Even if the balconies were sprinklered, there is still the hazard presented from the occupants carrying the 20-pound LP bomb up through the occupied building (including possibly using the elevators!) as well as the hazard represented from the disposal of the hot embers from a charcoal grill. The coals can appear to be out for several days but yet spark a fire when dumped into a trash can. (Can you say "garbage chute?")
Reply
Dan Wilder
5/6/2021 08:48:00 am
We exclude balcony protection (if it complies with the exceptions) with the requirement that a letter from the building owner (or a copy of the CC&R's) be provided that prohibits things like this and that gets submitted with our plans. If that letter cannot be provided, we will design & install protection on the patios via change order.
Reply
Franck
5/6/2021 09:31:43 am
Have a look at:
Reply
Dale Morris
5/6/2021 01:46:13 pm
I would provide, and let them be VE'd out. Many have said that BBQ grills are not typically allowed, and maybe someone won't haul a grill up to the 6th floor.......but I'll share the tragic story of a triple decker that went up in flames on Thanksgiving in our local area; someone was outside deep frying their Turkey on the back deck, and the fryer tipped over. Building was a total loss.
Reply
franck
5/6/2021 02:54:29 pm
Don’t worry, it is not because it is not allowed, that people don’t do it in Europe.
Reply
Casey Milhorn
5/6/2021 03:15:24 pm
Check out Myers Balcony decision tree document. He did a fantastic job with it. So many variables depending on construction type, year of code/standard enforced, and specific construction details of balcony. Then on top of that, you do get into local and state amendments to codes/standards that could change all of that.
Reply
Jay
5/10/2021 08:21:47 am
The IFC states:
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |