I have a parking structure that is sitting in the middle of an apartment complex. The bottom two floors are "podium" design and the architect is saying those floors are "enclosed" - thus requiring dry sprinklers throughout those floors.
Above the podium the garage floors are considered "open" and therefore I believe do not require sprinklers. Has anyone run into a similar situation? Perhaps with a parking structure that has underground portions and above ground portions? In those cases, what is the code logic for sprinklers in one area versus throughout? Thanks for any assistance! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Anthony
8/2/2022 07:04:27 am
Unless there is a fire/occupancy separation you must have sprinklers throughout a structure. I'd be very curious how you can have 2 separate garage areas? In general its poor design to work the code so you have partial sprinkler systems, no one likes that situation form first responders to maintenance.
Reply
Jesse
8/2/2022 08:09:32 am
My initial reaction is that this is a bad idea. I don't see how you would create adequate fire separation to justify a partial AS system.
Reply
Glenn Berger
8/2/2022 08:12:42 am
1) The new NFPA 88A requires all garages, open and enclosed, to be sprinklered.
Reply
Michael Millman
11/14/2022 03:03:06 pm
NFPA 88A is not a "referenced standard" in most jurisdictions, therefore it is not a code requirement. There are plenty of things that are good practice but are not code requirements.
Reply
RJ
8/2/2022 08:27:57 am
I have designed the same type of structure. It has a dry system on each of the three floors above grade, and also including the basement, where the fire pump and dry valve are located.
Reply
Todd E Wyatt
8/2/2022 08:32:56 am
The scoping Code that requires protection with an automatic sprinkler system (ASPS) is the adopted building Code (e.g. IBC and/or NFPA 101). The referenced standards (NFPA 13) inform how the ASPS is to be installed, inspected, tested, and maintained.
Reply
Alex
8/2/2022 02:48:45 pm
Hi,
Reply
sean
8/2/2022 08:51:52 pm
you need it everywhere. I had this come up caused a big change order.
Reply
Tim
8/3/2022 03:22:34 am
Traditionally the open ventilated floor could be done without sprinklers. The concern that we all are facing globally is that vehicle parking is no longer low risk because of Li-Ion batteries in electrical vehicles.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |