We have an open wood-truss concealed space above the highest ceiling and below the roof for a project that is getting sprinkler protection under NFPA 13.
The architect is proposing using spray foam closed-cell insulation to fill the entire concealed space. Does this qualify as non-combustible, such that filling the entire void would allow omission of sprinklers within this space? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
6 Comments
Franck
4/20/2020 11:11:28 am
If the entire space is filled, there is no possibility anyway to provide a sprinkler protection inside :)
Reply
Mike
4/20/2020 01:07:26 pm
Depends on the flame spread rating.
Reply
Jonathan Joseph
4/20/2020 05:03:20 pm
I believe most foam sprays are E-84 which does not qualify as One-hour fire rating.
Reply
Sean
4/24/2020 07:28:24 am
A one hour rating has no reflection on combustibility
Reply
Steven L.
4/21/2020 02:46:47 pm
You can look at NFPA 13 sec. 8.15.1.2.6 as a means to omit sprinkler coverage serving the structure. Refer to handbook for an illustration of the requirements that need to be met.
Reply
Rusty Scott
4/22/2020 03:26:02 pm
I've run into this question alot recently, architects are referring to using an intumescent and fire retardant coating. It's a paint-like coating that can be applied to structural steel, structural wood, and gypsum firewalls. It's intent is to reduce the rate of flame spread. I believe you can get it in white or clear, I would recommend white so that there is a visible indicator that it been applied. During high heat events the coating will expand and will look like it's charred. I would not believe this product can stay in place after it's exposed to a heat applied event and be reused, but I am unsure how post fire it would be removed unless it's scraped off. I would imagine if a fire's high heat was applied, the structural integrity would be in question and all would have to be replaced anyways. All the product information I've seen leads to it's use applying to satisfy NFPA 13 8.15.1.2.11.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |