I have a flat exterior canopy that projects 10-feet from the building, constructed of 2x solid wood joists, ceiling attached directly to the underside, roof sheathing directly to the top.
There is no storage beneath the canopy; the area below would be considered light hazard. I am having the architect change the sheathing attached directly to the underside from plywood to cement board, so I think I will meet the criteria to allow sprinklers to be omitted from beneath, per NFPA 13 Section 8.15.7.3 (2016 Edition), or Section 9.2.3.3 (2019 Edition), confirmed by the MeyerFire Canopy, Overhang, & Exterior Projection decision tree cheat sheet. (I realize I might have to take a closer look at the exposed material of the roofing.) NFPA treats the area below, and the concealed space within the canopy separately. There are the combustible concealed space exceptions. In my canopy, does the 4-foot width limit of 8.15.1.2.1.2 (2016), 9.2.1.19.2 (2019) mean I have to sprinkler the joists channels, or does the combustible concealed space omission of 8.15.1.2.5 (2016), 9.2.1.5(2019) overrule? NFPA 13 9.2.1.5 (2019): Concealed spaces formed by ceilings attached directly to or within 6-inches of ... solid member construction shall not require sprinkler protection. NFPA 13 9.2.1.19.1: Sprinklers shall be permitted to be omitted from within combustible... overhangs... that are constructed in accordance with 9.2.1.19.2 through 9.2.1.19.5. NFPA 13 9.2.1.19.2 (2019): Combustible soffits, eaves, overhangs... shall not exceed 4-feet in width. I’m thinking the section for sprinklering within canopies is more applicable to canopies with a larger void space within, that may not meet the usual combustible concealed space exceptions, where you’d have to make some minor modifications, no openings, and add draft-stopping to omit sprinklers from within the space. The architect said on a canopy similar to this one, they had to fill the 2x joists channels with insulation, but I don’t where code would direct us to do this, unless they were TJI’s. Does the 4-foot width limit specific to Exterior Soffits, Eaves & Overhangs overrule the Concealed Space Rules? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
15 Comments
Pete
9/27/2021 06:46:55 am
Are you in 2016 or 2019?
Reply
Alex
9/27/2021 07:35:46 am
Hi Anonymous,
Reply
Steven
9/27/2021 09:09:45 am
I might be missing something, but I agree with the original poster in that the requirements of NFPA 13 Section 8.15.7.3 (2016) are fully met in this situation, allowing sprinkler coverage below the canopy to be omitted (assuming the exposed roof material is limited-combustible). In addition, Section 8.15.1.2.3 (2016) permits sprinklers to be omitted from within the joist channels. It is my understanding thus that sprinklers would not be required in neither the concealed space nor the space below.
Reply
Steven
9/27/2021 09:42:44 am
Correction: I meant 8.15.1.2.5, not 8.15.1.2.3. However, I am looking at 8.15.1.2.18 and wondering if that will override the allowance of 8.15.1.2.5? I do think it would be very impractical to have to protect every joist channel, and would not meet the intent of the code.
Jesse
9/27/2021 09:10:45 am
Architects love their canopies.
Reply
SCHULMAN
9/27/2021 09:13:08 am
solid 2x wood joists = combustible construction ...
Reply
Dustin
9/27/2021 10:20:54 am
The 8.15.7 (2016) Exterior Projection provisions apply to both combustible and non-combustible construction whereas the 8.15.1.2.18 (2016) Exterior Soffits, Eaves, Overhangs apply only to combustible construction. The two sections speak to different architectural features but have no associated definitions as part of the standard.
Reply
Anonymous
9/27/2021 10:49:48 am
Generally, sheathing alone wouldn't matter as it's the entire construction per 8.15.7.2 (2016) 9.2.3.2 (2019) however the following section (2019 shown) allows another scenario, describing the "exposed finish material:"
Reply
David Kulbacki
9/28/2021 05:07:22 pm
I'm with you anonymous. I've addressed this situation by implementing 9.2.3.3 option (1), (2), or (3) for this kind of space.
Reply
Ritz
9/27/2021 11:54:46 am
I think the cart is before the horse here. What state are you in?
Reply
Mike
9/27/2021 04:59:03 pm
What did the estimator who landed the job plan for?
Reply
David Kulbacki
9/28/2021 05:06:55 pm
I've addressed this situation by implementing 9.2.3.3 (2016 edition) option (1), (2), or (3) for this kind of space.
Reply
Anonymous
9/29/2021 01:28:13 pm
Thanks, David (and all), I think you may have mixed the 2019 vs. 2019, but I see what you are saying, good point about the 3,000 sq. ft. It is often overlooked, that IF one takes advantage of one on the combustible concealed-space omissions, UNLESS you fit into one of the 11.2.3.1.5.2 (2016) / 19.3.3.1.5.2 (2019), you do trigger the 3,000 sq. ft. R/A for adjacent areas.
Reply
David Kulbacki
10/1/2021 10:49:07 am
Yes, my apologies, I meant 8.15.7.3 (2016 edition) not 9.2.3.3.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |