Do solar panels on a roof level of a parking garage require sprinkler protection?
The parking garage is six-level open air garage, and the roof level (the sixth level) is used for parking. Solar panels would cover 30% of the roof level and may potentially in future cover the entire roof. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
21 Comments
Pete H
5/20/2022 06:47:45 am
As in solar panels on top of the roof?
Reply
SCHULMAN
5/20/2022 08:23:04 am
i don't know of any code but these could have used some...
Reply
Dan Wilder
5/20/2022 08:29:05 am
We have been required to install them on the structural framing below the panels for one project and argued our way out of it on a couple others due to lack of structure and some creative help wordsmithing from the arch based on spacing and angle of the panels.
Reply
XIAO LI
5/24/2022 09:16:54 pm
Thanks for you answer. The PV panels are flat and with tiny gaps between modules. The slope is about 5%. The PV panels are installed on steel canopy structure looking like a roof a few meters above the roof.
Reply
Roy J.
5/20/2022 08:29:33 am
Are you looking at it as a concealed combustible space under the solar panels? It is an interesting question, there is no definition of concealed space in NFPA 13, but I don't believe it would not apply here, but as always the AHJ is the final authority. If it was decided it is a concealed combustible space there are some options to work through it without coverage, see 8.15.1.2.7.1 and 8.15.1.2.6 and most likely more...…remember my opinion is worth what you paid for it :)
Reply
XIAO LI
5/24/2022 09:19:08 pm
I could not relate to the space beneath the panels as concealed space. The panels are a few meter above the roof parking, acting like a roof canopy.
Reply
Glenn Berger
5/20/2022 08:30:58 am
The recently published NFPA 88A requires open parking garages to be provide with sprinkler protection.
Reply
Franck
5/20/2022 08:55:24 am
Even though solar panels represent a potential fire exposure to your roof assembly, there is no requirement to provide sprinkler protection.
Reply
Todd Wyatt
5/20/2022 09:20:46 am
The adopted building Code (e.g. 2021 IBC) is the scoping document that determines what Occupancy Classifications (e.g. Group S-2 Low-Hazard Storage) require an automatic sprinkler system. The referenced standards regarding spinklers per IBC Ch 35 (e.g. NFPA 13/13D/13R/16) are only applicable per the "prescribed extent of each such reference" as listed in the adopted building Code (IBC).
Reply
Franck
5/22/2022 10:47:43 am
I think that the question is not to protect the garage, but the solar panels on the roof of this garage
Reply
Todd E Wyatt
5/23/2022 08:34:04 am
The scoping Codes do not include specific components of a building (e.g. "solar panels") that require protection by an automatic sprinkler system in a building not required to be sprinklered. Sprinkler protection is per Occupancy Classification. The question refers to a "roof level" and not to an unoccupied roof so it is unclear. Parking garages are regulated by the number of "tiers" and not by "stories". If a parking garage is not required to have an automatic sprinkler system and the roof "tier" includes "solar collectors", it would not be required by the structure's Occupancy Classification to protect the rooftop solar collectors with an automatic sprinkler system.
Eric R
5/20/2022 09:26:57 am
This topic is definitely something that will need to be worked on at the model code level. I've been involved with two commercial rooftop solar fires where the fire was hot enough to punch down through the roof membrane and ignite the insulation on the interior side. Both of these buildings had sprinklers inside, so fire damage was limited on the interior, but even for the sprinklers it was a bit of the challenge as they aren't normally required to spray above themselves!
Reply
Andrew Thul
3/11/2024 09:10:16 am
California has developed code language for this in Chapter 9 of the CBC (speinklering under PV arrays)
Reply
Sanjeev Gupta
5/20/2022 09:31:04 am
Garage and parking area will require sprinkler protection due to associated fire hazard. But not required for solar panel as we donot see any thing fire hazard to burn there on panel.
Reply
Franck
5/22/2022 10:50:14 am
There has unfortunately been a number of fires with solar panels on roofs. They definitely do present a fire hazard by themselves. And a fire exposure if the fire can then spread to the roof itself.
Reply
Jack G
5/20/2022 07:03:37 pm
I recall a rooftop fire, years ago, NJ, Morestown, where firemen couldn’t get on the roof—- electricity from sun, water, humans.
Reply
sean
5/20/2022 07:40:15 pm
no
Reply
Franck
5/22/2022 10:51:19 am
That’s a good summary
Reply
Alex
5/24/2022 06:08:55 am
Hi,
Reply
XIAO LI
5/24/2022 09:35:21 pm
Hi All, thanks for the replies. It is a surprise there are so many great comments. Some additional information about the building. The parking garage is located in Canada. It is a six-tier/level open-air parking garage proposed to be mass timber CLT floors with concrete topping. Columns and beams are mass timber as well. The building is proposed to be fully sprinklered. However, the code does not require a concrete building of the same size to be sprinklered. Sprinkler protection is a mitigation measure in order to get approval from the AHJ.
Reply
Christopher Anderson
6/2/2022 12:36:48 pm
Buildings based on the NBCC model code defines a building as follows:
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |