We are working on a new electric car factory. Under the 2018 IBC, it's classified as an F-2 occupancy. Earlier we had provided ESFR sprinklers in these buildings.
Since there is no specific requirement for smoke removal for an F-2 occupancy, we want to provide standard response or quick response sprinklers instead of ESFR, by classifying parts of the building as Ordinary Hazard Group 2 (OH2) in NFPA 13. Is this reasonable for all areas? Production areas? Would an OH2 classified space require smoke removal? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Anthony
2/14/2024 07:54:04 am
OH2 is reasonable for all the non battery dense areas. I'd suggest no less than EH1 for ay areas where the battery skid is attached to the cabin. I'd suggest EH2 in any areas where the battery skid is assembled.
Reply
Glenn Berger
2/14/2024 08:20:23 am
Classifying the entire facility as F-2 would not be appropriate. Neither would OH2 be appropriate for the entire facility.
Reply
Jesse
2/14/2024 08:33:48 am
Manufacturing facilities commonly have multiple occupancy hazard classes, and as such are protected with different design approaches. I wouldn't look at the entirety as F2. Raw material storage may be protected one way, manufacturing may be OH 2, and finished product may again be protected as storage.
Reply
Todd E Wyatt
2/14/2024 11:06:54 am
Correct Occupancy Classification (OC) per IBC-2018 = Group F-1
Reply
Todd E Wyatt
2/14/2024 11:07:46 am
REFERENCES
Reply
Jaber Alhaji
2/14/2024 11:05:36 pm
Thanks all for your insights. Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |