We're currently working on a school project. There's a suspended ceiling throughout much of the school. The project requires "total coverage", but I'm not sure whether this applies above the ceiling, below the ceiling, or both.
We're under NFPA 72, but 72 does not seem to clarify this either way. Are smoke detectors required above and below ceilings, for "total coverage"? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Jon
2/2/2022 08:07:39 am
2016 NFPA 72 17.5.3.1 "...total cover-age of a building or a portion thereof, shall include all rooms, halls, storage areas, basements, attics, lofts, spaces above suspended ceilings, and other subdivisions and accessible spaces." sections 17.5.3.1.1-17.5.3.1.5 offer modifications/exceptions, might want to read through those and the annex language.
Reply
2/2/2022 08:08:15 am
Is the building sprinklered in accordance with NFPA 13?
Reply
Glenn Berger
2/2/2022 08:09:17 am
It comes down to what items are in the attic:
Reply
Brian Gerdwagen FPE
2/2/2022 08:38:49 am
Jon is correct for the definition of "total coverage." I believe the issue isn't "is smoke detection required in the attic per code?" it is "the project requires total coverage and what does that mean?"
Reply
Todd Wyatt
2/2/2022 08:41:30 am
The IBC (or the NFPA 101 Life Safety Code) would be the scoping Code for automatic smoke detection system (ASDS) in Group E Education occupancies per 907.2.3. This section identifies where manual fire alarm systems are required and includes exceptions IF automatic sprinkler systems are installed throughout but does not include a requirement for an ASDS to be installed "throughout."
Reply
Jay
2/2/2022 10:25:27 am
Ask the AHJ what they are requiring.
Reply
Pari M Bagayee
2/2/2022 10:31:30 am
NFPA is a standard for installation of fire alarm system is not the code requirement , as Todd mention IBC should be the guideline.
Reply
AHMED MOUSTAFA
7/5/2022 06:47:19 am
Hi can you send me something indicate that in the code
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |