We are installing an elevator (freight) at an advanced water treatment plant. The doors open at two locations:
Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Jonathan Griffin
9/5/2022 08:15:22 am
In your case, a 190'f Heat Detector is usually called out for Elevator Capture.
Reply
Chad
9/5/2022 08:16:34 am
In the states I work in smokes are only required if the elevator is rated for passengers. Freight only no smokes/recall etc. but if a landing for passengers is outside, you’d need a heat, not a smoke.
Reply
Glenn Berger
9/5/2022 08:18:12 am
Not sure what the awning in question looks like or where you are located, smoke detectors may not be appropriate for your project. For outdoor locations, some AHJs will not require a detector to be placed.
Reply
Alex
9/5/2022 09:12:44 am
Hi,
Reply
DS
9/6/2022 06:44:04 am
10.3.5
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop March '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |