If NFPA 75 isn't an explicitly adopted code by the AHJ or not referenced by any of the other applicable codes is smoke detection required in a raised floor area?
NFPA 72 provides location guidance but other than that I can't find in NFPA 101/IBC where smoke detection would be required in the raise floor space. Not every jurisdiction/client adopts NFPA 75, I'm unsure what other code or standard would require below floor smoke detection. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Sanjeev Gupta
5/13/2022 08:09:52 am
It is logical to provide smoke detector under raised floor due to fire risk related to electrical cables.
Reply
Franck
5/13/2022 08:12:46 am
I don’t know if it is required by code in the US, but this is definitely a good practice as a quite important combustible load might be present (cables).
Reply
Glenn Berger
5/13/2022 08:13:32 am
Need to know what items are located below the raised (access?) floor.
Reply
Jesse
5/13/2022 08:17:01 am
NFPA 75 is indeed the standard. And I don't envy the position you're in.
Reply
Danial Bartle
5/13/2022 08:24:03 am
If the jurisdiction has adopted NFPA 1, NFPA 75 is also incorporated by reference.
Reply
Todd E Wyatt
5/13/2022 09:00:51 am
Jurisdictions (federal, state, county, municipality, etc.) will adopt Building Codes (e.g. ICC ... IBC, IFC, IMC, IPC, IEBC ...) and/or Fire Codes (e.g. NFPA ... NFPA 1, NFPA 101 ...) which include other standards (e.g. NFPA 75) by reference :
Reply
Alex
5/13/2022 09:03:43 am
Hi,
Reply
Ronnie
5/13/2022 10:22:07 am
It's my understanding that the building of fire code identifies which occupancies require a fire alarm system and NFPA 72 tells you the how to install and the location to install.
Reply
Loren Rocha
5/16/2023 09:39:44 am
Does NFPA70 Article 645.4&5 allow you to ignore the low smoke requirement of NEC Article 300.22
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |