We have very deep beam glue-laminated timber construction that just has the laminated wood exposed to below. The beams are very deep; 2'-9" deep. These form bays that are 13'-9" x 13'-9", many with smooth ceilings. The area below is light hazard. Can sidewall sprinklers be used up in these coffered areas? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
3/21/2023 07:04:02 am
Not really conceivably.
Reply
Pete H
3/21/2023 07:09:23 am
...21 minus 14 is 7, not 5. Let's just pretend that's a typo.
Reply
Dan Wilder
3/21/2023 07:50:31 am
Can you, sure. Need to confirm the lower perimeter soffits bounding the bays are less that 16",so providing a back to back installation is feasible within every pocket (13-22' 10.3.4.1.4.1 -The maximum width of the lintel or soffit shall not exceed 16 in. (400 mm).)
Reply
Jesse
3/21/2023 09:03:35 am
Wow that's a mess. I think Dan's on the right track in finding an allowance to do it. I just don't think its the best means to protect this area. I think I'd be looking at other options.
Reply
Paul Pinigis
3/21/2023 09:23:36 am
Yes, you can treat each bay as a room and protect it with a sidewall.
Reply
HASSAN ABDALLA
3/23/2023 05:26:29 pm
That is what I was thinking considering pockets like room each.
Reply
Dave
3/21/2023 11:00:38 am
I assume beam penetrations (for the sprinkler lines of for back-to-back sidewalls) are out of the question, and I assume the architect is going to want the sprinkler lines running off to the side of the cells. I am also encountering similar configurations in historic buildings (e.g. McMenamins) with plaster coffered cells like this, and see effective use of sidewalls, horizontal or vertical, paying particular attention not to exceed the maximum deflector to back wall distance. I expect to see a lot of new challenges with new forms of engineered lumber, CLT, DLT, mass timber, etc.
Reply
Dave
3/21/2023 11:03:06 am
...But are there obstructions including those created by surface-mounted lights?
Reply
Glenn Berger
3/21/2023 11:15:47 am
Based on the dimension you provided, each pocket requires sprinkler protection.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |