A dormitory has 1/2-hour fire barriers separating each residential unit. On each side of the 1/2-hour wall, penetrating the 5/8" gypsum, are shower valves that serve showers within bathrooms on each side.
The shower valves have the valve assembly itself and an opening that's covered with a metal escutcheon. These would qualify as a membrane penetration under the International Building Code. For back-to-back vales in the wall, how is this commonly addressed to still maintain the 1/2-hour fire resistance rating? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Mike
5/17/2019 02:02:44 am
Go to the hilti website and they have UL Listed details for fire-resistive penetrations.
Reply
Mike
5/17/2019 02:15:24 am
Here's two more links
Reply
sean
5/17/2019 08:43:51 am
here a enclosure
Reply
WES
5/17/2019 08:50:19 am
This project is Type II-B construction and is sprinkler-protected throughout per NFPA 13, so it qualifies under the little-used (I'm sure) exception 2 of IBC 708.3 (2012 Edition).
Reply
1/22/2020 03:48:59 am
Such a great article you had posted. I think that would help me a lot.thanks for sharing this post. Keep posting like this.good wishes.. 🙂
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |