Under NFPA 20, Section 4.20.7.1:
The circulating relief valve shall actuate below the opening set point of the pressure relief valve to ensure cooling of the pump during churn operation. NFPA 20 Handbook: The pressure setting of the circulation relief valve should be well below the pressure relief valve setting but above the maximum suction pressure. Based on this, how do I properly specify the circulation relief valve setting that is installed on the pressure relief valve discharge line if the pressure relief valve set point is 175 psi? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Nick Devine
3/23/2022 08:19:15 am
The circulation relief valve is intended to operate on the start up of the fire pump to keep the casing cool when the pump is running at a no-flow condition (churn).
Reply
Franck
3/23/2022 08:37:44 am
Perfect explanation by Nick
Reply
Jack G
3/23/2022 09:01:56 am
It all depends on design pressure. A lot of Engineers now, design to 175 psi.
Reply
Tim Darling
3/23/2022 09:24:02 am
It is not really practical to try to preset a circulation relief valve at a given pressure. Make sure the circulation relief valve you order is within the pump pressure specs. That is the most common mistake made when it comes to circulation relief valve.
Reply
Jesse
3/23/2022 10:10:37 am
I started to reply, then got busy. The refreshed my screen and saw that Nick had a most excellent reply. Nothing to add
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |