We have a non-conforming fraternity building that wants to build a new two-story covered entrance canopy that ties into the existing roof. It is a heavy timber construction and has no concealed spaces. The fire area is already too large, so our interpretation is this would trigger a sprinkler system in the whole building.
A more lenient interpretation might be to only sprinkler the new portion, and potentially add some rated separation between the existing non-sprinklered building and the new sprinklered entry canopy, but I am not aware and I can't find anything about separation between sprinklered and unsprinklered portions of a building. Would this arrangement be permissible by code? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
3 Comments
James
12/16/2019 01:40:48 pm
For only the new portion to be protected and not the entire existing facility, the new entrance structure would need to be considered as separate "building" by code.
Reply
Joe
12/17/2019 02:38:05 pm
Thank you James for the response!
Reply
10/3/2021 08:05:48 am
James, what about IBC Chapter 3105 Awnings & Canopies provisions. Special Construction is not considered as separate buildings.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |