Hi all, is anybody aware of a sealed sprinkler that is available in the market with an elongated spray pattern?
I'm looking for something specifically designed for conveyor protection. Have tried the main manufacturers (Reliable, Tyco, Viking etc.) but nothing seems to be out there. The FM data sheet (FMDS0711) suggests that they are out there. Many thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Jesse
12/22/2022 08:08:29 am
I learned long ago that just because the code (NFPA or FM) suggests a certain sprinkler may be used, that doesn't mean said sprinkler exists yet, or ever will.
Reply
Glenn Berger
12/22/2022 08:36:59 am
I have always just used standard spray sprinklers, open or closed type based upon site specific conditions.
Reply
Franck
12/22/2022 08:38:42 am
I do agree with Jesse
Reply
Jesse
12/22/2022 08:47:47 am
I too have always just used standard spray sprinklers. And while not part of the sprinkler discipline per se but rather the overall fire protection engineering of the facility, Glenn touched on a very important point. These are moving - usually pretty fast. We know that numerous areas of ignition creating a bunch of little incipient fires along the way that grow to become bigger fires will overwhelm the water supply pretty quick. That interlock to shut it all down on water flow is pretty critical.
Reply
Shane
12/22/2022 09:37:13 am
I agree with the above. Also, corridor and attic sprinklers are listed for light hazard use only. Conveyors are usually in ordinary group 2 and higher hazards. Stick with the Standard Spray Sprinkler Heads.
Reply
Matt C.
12/22/2022 09:42:35 am
The ONLY sprinklers I have come across that have narrow spray patterns like this are corridor/hallway sprinklers, which are obviously NOT designed for this application. They do however have crazy long coverage areas in the neighbourhood of 28'x10' or 28'x12' (see Viking VK638, Reliable RA5814, Tyco TY4282).
Reply
Dan Wilder
12/22/2022 10:40:27 am
I think the wording of sealed is not referring to a closed head sprinkler but sealing the opening through an enclosed conveyor. It's not a smoke/heat/fire barrier and does not have to be rated so we have utilized everything from a 2" coupling rubber turned inside-out over a 1.5" pipe to having their sheet metal guys cut a horseshoe out of scrap and Tek screw it to the shroud
Reply
Alex
12/22/2022 02:09:20 pm
As others have mentioned, I do not believe there is an extended spray sprinkler for this application.
Reply
Dwight Havens
12/24/2022 02:34:42 pm
I would like clarification of the meaning of "sealed". If it means closed head, the use of directional nozzles, like the Tyco EA-1 may be appropriate. If looking at an open head nozzle, a Tyco D3 might work. Other manufacturers also may have them in their catalogs.
Reply
Phil Watkins
12/28/2022 03:46:43 am
Hi all and many thanks for the input on my question. Just to clarify, I did mean a sealed sprinkler (i.e. thermal bulb or soldered strut) as opposed to an open nozzle.