We have a paper plant that has storage of rolled tissue paper stored up to 16-feet. While researching the protection requirements in NFPA 13 I discovered this commodity class at these heights can be protected by CMDA designs, but not CMSA or ESFR. I have been unable to find why CMSA and ESFR isn't allowed in NFPA 13 (handbook and other resources).
Do you have any idea why CMSA and ESFR wouldn't be permitted for this hazard? Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
1 Comment
Mike
3/12/2021 10:31:59 am
Have you check Chapter 19? From what I see in NFPA 13 and the Tyco ESFR 25 Data Sheet, rolled paper storage is permitted to be protected by both ESFR and CMSA.
Reply