I am a municipal fire inspector. We have a new high school, fully sprinklered, that has residential stoves in a classroom. These are protected with UL300A hoods.
Are these hoods required to be connected to the fire alarm? Common sense would indicate that if there was a fire hot enough to release the UL300A system, that the building occupants could be in danger and the fire alarms should activate, however, I cannot find a code reference for this. The architect is saying the stoves are residential so only residential requirements apply. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
8 Comments
Glenn Berger
9/4/2020 10:19:43 am
The systems shall be monitored. The application is not for a residential use, but for public use!
Reply
Jonathan Joseph
9/4/2020 10:22:48 am
It's not residential it is E occupancy.
Reply
Bill Jones
9/4/2020 10:30:49 am
2017 NFPA 96 10.6.2 states “Where a fire alarm signaling system is serving the occupancy where the extinguishing system is located, the activation of the automatic fire-extinguishing system shall activate the fire alarm signaling system.
Reply
Mahmoud Badr
9/5/2020 03:19:37 am
Agreed.
Reply
Bill
9/4/2020 10:37:05 am
If your jurisdiction subscribes to any fire code derived from the IFC, please see Section 904.3.5.
Reply
Dallas Soles
9/4/2020 10:45:59 am
The jurisdiction that I work for has allowed several of these to be installed. The intent of allowing the UL 300A type of hood with a built-in preengineered suppression system is to fulfill the requirements NFPA 96, and allow the residential range be installed with a residential type of hood. This includes the fire alarm requirement of NFPA 96 if a fire alarm exists. Most of the systems have a pair of dry contacts that is a relay to be tied to the fire alarm.
Reply
Jerry Clark
9/4/2020 10:46:58 am
Look at IFC Section 904.3, specifically 904.3.5
Reply
Randy Kimbro
9/4/2020 11:27:16 am
Thank you to each of you for the input. That helped point us in the right direction. Our jurisdiction uses the IFC along with the Ohio Fire Code. We are going with those (904.3.5 in both) as well as NFPA 72 Section 17.14. The NFPA 96 comments above were also right on the money and an area we did not see before. The Scope 1.1.1 and 1.1.2 have wording that apply specifically and exactly as well as 10.6.2 mentioned above. We appreciate the research help.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |