I have a fire hydrant in a planter curb, and we will have some trash enclosures nearby.
What is the required minimum clearance for a trash enclosure wall from the hydrant itself? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Brett
3/25/2021 09:16:47 am
NFPA 1 2018 Edition
Reply
DARIN
3/25/2021 09:18:09 am
IFC/CFC 507.5.5
Reply
Jonathan Sullivan
3/25/2021 09:33:40 am
Note that IFC does not require the clearance in front of the connections.
Reply
Manny Rios
3/25/2021 10:28:12 am
NFPA 1 Fire Code 2018 Edition requirements for hydrant clearances are not required, unless specifically adopted as noted for the state of Florida and elsewhere.
Reply
Keith White
6/29/2022 09:55:13 am
What are the clearance requirements for an indoor fire hydrant in a commercial building?
Reply
Freeman R. Jones
5/16/2023 03:18:19 pm
is there a larger set back from a fire hydrant and a street lamp post?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |