I was asked to evaluate a warehouse that was built in 1996 for a new racking permit.
The original fire sprinkler system was designed with ESFR sprinklers with a K factor of 14.0. During the evaluation I found that the building peak was 40'-0" tall. Knowing that NFPA 13 no longer allows K-14 ESFR sprinklers in a building over 32'-0", I informed the building owner that the existing sprinklers need to be replaced with a larger-orifice ESFR sprinkler. The building tenant has tried everything they can to find away around this and does not understand why the building is not grandfathered. I am just curious if anyone else has encountered this situation and what the outcome was. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
16 Comments
Dan Wilder
9/23/2021 07:57:30 am
The area of the new racking would need to be upgraded but areas outside of that scope should be excluded...however, in many cases (justifiably in most of them) this provides the AHJ the means to require building upgrades. Has the AHJ adopted the newer NFPA that removed the allowance (I'm assuming so but it's an argument if not)
Reply
Glenn Berger
9/23/2021 08:09:29 am
Situation is always ugly. Good Luck
Reply
matt
9/23/2021 08:30:32 am
I have found on occasion that swapping out k14's for k16.8 ESFR heads will still function hydraulically and also will provide updated coverage criteria. That has been a less-expensive route for upgrades. That or in-racks for the revised storage plan.
Reply
matt
9/23/2021 08:33:14 am
...also, it is technically grandfathered right now since they are using the facility under outdated design criteria with their current permit. If they need a new racking permit, then it is a new use. You can't "grandfather" a new use. (generally)
Reply
Alex
9/23/2021 05:12:46 pm
My thoughts exactly ^
Reply
NK
9/23/2021 08:34:14 am
We run into this often. 14K ESFR heads were really popular in our area in the early 2000's which is terrible when tenants change. If new racks are being added or modified to an existing warehouse we usually don't have problems matching the existing design criteria, but new use and occupancy typically requires the system to be brought up to the currently adopted NFPA 13 standard. Most of these buildings have fire pumps so there are multiple things you can do to upgrade the existing system without significant modifications. Consider in-rack options if you don't have a fire pump. Talking to the local AHJ first is usually a good place to start.
Reply
M
9/23/2021 08:38:58 am
Could you consult with the AHJ to allow the use of FMDS 8-9?
Reply
Jesse
9/23/2021 09:00:31 am
I strongly dislike the "grandfather" concept. We've always operated under the "fire doesn't care about your grandfather" mode.
Reply
Franck
9/23/2021 12:27:19 pm
Fully agree with Jesse regarding the "grandfather" concept.
Reply
Matt
9/23/2021 09:06:50 am
be sure to review the specifics in the FM data sheets before trying to use those criteria. The FM discharge requirements can be much higher than NFPA.
Reply
Bob
9/23/2021 11:15:10 am
Upgrading or changing out racking is different than a change of use and does not necessarly mean an increased hazard. We have hit similar situations related to smoke venting and tenant changes in existing warehouses.
Reply
Joshua Freedman
9/23/2021 04:41:57 pm
As a property consultant for an insurance company, I often have to tell building owners that we honestly don't care if the City says they are grandfathered in for one thing or another, the City isn't going to pay for the damages caused by a fire. If I have to rate a sprinkler system as inadequate, they can see their insurance rates double which can be quite a lot of money and puts the investment of a few sprinkler heads into a different perspective. Also, the cost of doing the upgrade now while you are out there and have the engineering and permitting going on is going to be a lot less that if they have to do the update down the road and start from scratch. Just from a cost/business perspective, it would probably be in their best interest to upgrade.
Reply
BOB
9/24/2021 09:11:39 am
I think Joshua makes a very valid point from about the insurance issue and I have heard it often "in the field".
Reply
Brian Gerdwagen FPE
9/24/2021 08:54:43 am
To make a real quick point:
Reply
Stef
11/12/2022 04:19:43 am
Is it technically easy to remove current K14 heads by bigger orifice ones (K17 or even bigger) considering threadings are different... ?
Reply
Andrew Valente
4/27/2023 09:55:08 am
k14 and k17 (16.8 actually) are almost always 3/4-inch thread.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |