Is the minimum length for a remote area determined by the original Density/Area (such as 1,500 sqft so it would be 46.5 ft), or is it based on a modified/adjusted area (such as 900 sqft = 36 ft).
After doing this for years, I was trained and always took is as a given that we use the length based on the original area. I cannot seem to find an actual reference backing this up. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Pete H
3/15/2023 06:47:20 am
I don't have any code reference on hand, but the way I've been trained is the longest distance in your remote area is orientated to run parallel to the branches, and the shorter distance of your rectangle to run perpendicular to that.
Reply
Dan Wilder
3/15/2023 07:32:42 am
NFPA 13 - 22'
Reply
danefre
3/15/2023 08:22:38 am
Dan and Pete nailed it.
Reply
David Kendrick
3/15/2023 09:47:36 am
NFPA 13 - 2016 Annex
danefre
3/15/2023 10:24:56 am
Thanks for the reference. I'm glad the annex has an example.
Glenn Berger
3/15/2023 08:15:02 am
I am not quite sure what your question is implying. If you have a renovation project that requires sprinklers to be replaced / relocated and with piping reconfigured then you need to verify that the original conditions are not affected from the design.
Reply
Anthony
3/15/2023 10:30:13 am
As others have said, and I agree, the length of the longest side of the remote area along a branch line should be based on the modified area.
Reply
sean
3/15/2023 12:03:38 pm
The final area is what determines the width.
Reply
Franck
3/15/2023 12:07:34 pm
It has to be done on your final design area.
Reply
DAVE
3/15/2023 12:07:53 pm
Agreed, it's 1.2 x the square root of the adusted. I have always explained to trainees that once the final size of the remote area is determined, the multiplier adjusts a theoretical perfectly square fire into a more demanding NFPA 13-required rectangular remote area, and aligning with the branch lines to pick up more sprinklers usually (but not always) creates a greater system demand.
Reply
Alex
3/16/2023 05:57:47 am
As others have mentioned, you use your final area when determining branch lines and number of heads. Same goes for dry or pitched systems.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |