The International Building Code Section 707.5.1 (2015 Edition) requires structure to have at least the level of fire resistance as the element it is supporting:
707.5.1 Supporting construction. The supporting construction for a fire barrier shall be protected to afford the required fire-resistance rating of the fire barrier supported. Hollow vertical spaces within a fire barrier shall be fireblocked in accordance with Section 718.2 at every floor level. Exceptions: 1. The maximum required fire-resistance rating for assemblies supporting fire barriers separating tank storage as provided for in Section 415.9.1.2 shall be 2 hours, but not less than required by Table 601 for the building construction type. 2. Supporting construction for 1-hour fire barriers required by Table 509 in buildings of Type IIB, IIIB and VB construction is not required to be fire-resistance rated unless required by other sections of this code. The project is a three-story hotel and each unit is required to have a 1/2-hour fire resistance rating between units and between the unit and the corridor. Is the building structure required to have at least a 1/2-hour rating on account of these separations? I see two potential outs that would not require it - first being that the 1/2-hour fire resistance rating could be considered a "fire partition" and not a "fire barrier". Second out is exception #2 listed above although it speaks to a 1-hour rated fire barrier and not a 1/2-hour fire barrier. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
0 Comments
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |