NFPA 13 (2019) Section 9.4.3.2 states that quick-response sprinklers shall not be mixed with any standard-response within a compartment unless some conditions apply.
9.4.3.2 Where quick-response sprinklers are installed, all sprinklers within a compartment shall be quick-response unless otherwise permitted in 9.4.3.3, 9.4.3.4, or 9.4.3.5. Those conditions don't apply in my case and I know there's a definition of a compartment in 3.3.38. However, from a practical standpoint if the compartment in question is a corridor, would you include the adjoining offices in the compartment? These offices are likely to have their doors open and are not on any magnetic door closing devices. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
6 Comments
Wayne Ammons
4/22/2020 08:22:40 am
A compartment can have openings to the adjoining space up to 8 ft. wide as long as there is an 8" lintel from the ceiling and a single opening (such as a door) 36" wide without a lintel. Is your scenario different than what the definition describes?
Reply
Dan Wilder
4/22/2020 08:38:14 am
Change the sprinklers in the corridor to all be SR (match existing conditions I am assuming) unless the adjoining offices also do not comply with the definition of a compartment, then you are on the hook for the complete change out. This is allowed per 9.4.3.1(5).
Reply
Franck
4/22/2020 10:28:42 am
I won't be too much concerned in your case.
Reply
Mike
4/22/2020 03:35:18 pm
What is the occupancy? If it is light hazard, aren't QR heads required?
Reply
Daniel
4/23/2020 04:44:28 pm
It would normally be light hazard but it's ordinary based on the jurisdiction. The issue is the ones in the corridor need to be changed to QR out to deal with a ceiling pocket issue. The question is if the ones in the adjoining offices also need to be changed since typically people have the doors open. While I don't think they have to per the compartment definition, it may be practical to do so.
Reply
Mike
4/22/2020 08:37:40 pm
If the OP is talking from a practical standpoint, use QR response matching QR sprinklers already installed.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |