Is a pumper truck from the fire department required to do standpipe flow testing?
Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
20 Comments
jay richardson
3/2/2021 09:10:23 am
Assume you are asking in regards to a manual standpipe.
Reply
Matt
3/2/2021 09:14:13 am
one time we had to rent a large pump on a trailer because the FD required a test, but refused to provide a pumper truck.
Reply
Mike
3/2/2021 09:15:55 am
NFPA 25 6.3.1.1:
Reply
Peter
3/2/2021 09:35:09 am
It's important to note that connected to a water supply doesn't necessarily mean the standpipe is 'automatic'. Most of us understand that a standpipe fed from a 3/4" line is just a manual wet standpipe (obviously not automatic). However, it can be challenging to determine if the standpipe is automatic or not if you don't have the plans. For example, an unsprinklered building that is 6 stories (less than 75') and has a class III standpipe may be an automatic standpipe but have flow rates equivalent to a class II standpipe per NFPA 14. That same 6 story building with a fire pump and fully sprinklered may have a manual class I standpipe. Performing 5 year inspections without having plans or a calc plate that says it is a manual standpipe or shows the flow rate required can be tough.
Reply
sean
3/2/2021 02:13:39 pm
per NFPA 14 all standpipe systems need acceptance testing to match the calculated flow.
Reply
CJ Bonczyk
3/2/2021 09:19:54 am
Assuming the system is not automatic. 11.5.1 of 14 Ed. states to verify system demand, this can be waived by the AHJ. 11.5.2 For a manual standpipe, a fire department pumper, portable pump of a capacity to provide the required flow and pressure, or other approved means shall be used to verify the system design by pumping into the fire department connection.
Reply
Keith A Heckler
3/2/2021 09:24:22 am
A FD vehicle is not necessary but somehow you need to create the flow and pressure. The flow and pressure at the discharge needs to be measured. I have seen portable pumps on trailers used at the FD connection and, if a building has a fire pump, it can also be used.
Reply
Jesse
3/2/2021 09:49:30 am
Thankfully the AHJs in our area that require the flow testing also provide a Engine Co. to conduct the test. Without that, I guess we'd have to figure something out.
Reply
Mike
3/2/2021 10:19:01 am
Reference NFPA 14 for the definition of an AUTOMATIC system:
Reply
Mike
3/2/2021 10:21:06 am
Also reference testing requirements per NFPa 14:
Reply
Jay Richardson
3/2/2021 11:41:10 am
System type doesn't matter for acceptance testing
Reply
Robert Bennett
3/2/2021 01:15:58 pm
System type does matter because an automatic standpipe must provide the 100 PSI residual without FDC support. IE High rise
Jay Richardson
3/2/2021 11:17:08 pm
In regards to when flow testing is required...system type does not matter for acceptance testing, all types are required to be flow tested....system type does matter for 5 year testing of existing systems, automatic systems are required to be flow tested whereas manual systems are not
JOHN M ERCOLANO
3/2/2021 11:46:38 am
We have been performing MWSD tests for the AHJ's and othe SPK contractors in NY for the last 8 years. We purchased a used fire pumper truck, 4- 2.5" hose monsters and hoses. At the top of the furthest SD install two- 2.5" FHV connections and a gauge run hoses out of the building and connect to the 2- hose monsters they must provide 500gpm @100psi. Repeat the same at the top of each other SD with one FHV, run hoses out of building to 1- hose monster, each of them must provide 250gpm @100psi. Connect the 5" suction hose from hydrant to the fire truck and multiple 2.5"hoses as required from truck to the buildings FDC connection. Adjust the RPM on truck and throttle FHV on SD until proper GPM@PSI is reached. 3men @ $4750/test paid upfront if working for another sprinkler contractor LOL.
Reply
Dave Sornsin
3/2/2021 10:04:56 pm
John E:
Reply
JOHN M ERCOLANO
3/3/2021 11:48:18 am
99% of the MWSD tests are on 4story or less buildings and the limit of the test is 1000gpm at 100psi, we have never fell shoot meeting the requirement since I can just rev up the pumpers rpm's and make pressure and flow. So far so good, most of the fire marshals are happy seeing 100psi at the top gauge and 45psi on the hose monster pitot gauge using 1-1/8"orifice. Good luck out there!
Jason
3/24/2022 09:32:50 pm
We are dealing with an engineer that is claiming the additional pressure added by the pumper truck is providing a pressure in excess 175 psi. We tried to explain that there isnt actually that type of pressure on the system because the system is open and flowing water. Is there something in the code that “exempts” this testing from the 175 psi limit? Similar to how a 200 psi hydro test doesnt create a problem even though it exceeds 175 psi? Any help would be appreciated.
Reply
Dave Sornsin
3/2/2021 10:42:49 pm
To answer OP: Since Mr. Ercolano and truck are on the other coast, we use the FD's pumper truck and crew. Some FD's charge, others do it for free. We have HM's, calibrated gauges, rent a ton of hose, and have at least 6 people on site for valve spinning and gauge reading.
Reply
JOHN M ERCOLANO
3/3/2021 11:33:49 am
Most of the FD will not perform this test do to liability issues.
Reply
In my locale for a manual standpipe I have only seen a requirement for a visual requirement on an annual basis. There is also the 5-year requirement for a flow test. For the flow test I will reach out to the AHJ and explain my role as a facility's <a href='https://www.fireprotectionlincoln.com/'>fire protection</a> contractor and ask if they will bring a truck on site while we are there.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |