Is there a standard spacing for private fire hydrants?
No applicable code for this project, but looking for guidance in what would be common under NFPA 24, NFPA 1 / 101, and/or the IBC. Thanks in advance. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Ryan D Grant
9/3/2020 10:06:22 am
No more than 600 ft. Most fire apparatus carry 800 ft LDH. Should also check with the AHJ about connections. They may also provide spacing guidelines.
Reply
Randy Childress
9/3/2020 10:12:48 am
This is covered in IFC 218. It is park of the appendix sections. Table C102.1 and Appendix C103
Reply
David Buell
9/3/2020 10:20:42 am
NFPA 850 - 300 ft spacing for main industrial areas, 500 ft spacing for remote areas
Reply
Robert B.
9/3/2020 10:59:54 am
NFPA 101 does not contain any requirements for hydrants. Since you state no codes are applicable, I would say you have a choice of IFC or NFPA 1. I would look at Chapter 18 of NFPA 1 or Chapter 5 and Appendix B in the IFC. Outside of that, you may also want to consult with the property insurer to see if there are any requirements they may have that exceed minimum code. Also consult with the local FD to assess their capabilities and if going above minimum requirements would better accommodate their ability to address this facility you are dealing. Regardless of which code you use, you might need to assess the required fire flow (RFF).
Reply
SK
9/3/2020 04:51:07 pm
In line with IFC, Fire hydrants should be spaced at a maximum of 90 meters (300 feet) from each other along the travel path of the adjoining roadway available for use by fire apparatus. A fire hydrant capable of meeting the system demand must be located within 30 meters (100 feet) of any required fire department connection installed in a new building.
Reply
Manny Rios
9/4/2020 08:45:44 pm
The spacing/location of the fire hydrants would depend on the fire-flow requirement and number of hydrants required. See Appendix C sections C102, C103, and C105 of the 2012 International Fire Code.
Reply
3/4/2022 01:35:26 pm
If any industrial building has designed to install wet type Indoor Class III - Fire Hydrant or Standpipe system,
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |