Can anyone point me in the right direction for codes pertaining to the construction of a draft curtain?
My client will be installing them as part of an attic design, where draft curtains are required per the sprinkler listing. The sprinkler data sheet covers the depth requirement of the draft curtain. From browsing some websites I can gather they can be constructed of fire-resistant fiberglass woven textiles, glass (smoke baffles), or even panels of sheet metal. Does NFPA or the IBC define how they are to be constructed? My client will most likely use sheet metal. I'm curious if there is a gauge requirement for the metal. I may be overthinking it, but I like to see the code defining the curtain requirement, to avoid the contractor putting the wrong materials in place. I appreciate any help that anyone can provide. Thank you. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H
5/9/2022 06:45:27 am
From NFPA 13 (2016):
Reply
Jesse
5/9/2022 08:17:26 am
Good question. I'd refer to NFPA 204 where it talks about draft curtains, though I don't recall it specifying a minimum gauge for sheet metal.
Reply
Todd E Wyatt
5/9/2022 08:17:31 am
Per 2021 IBC :
Reply
Todd E Wyatt
5/9/2022 08:21:03 am
The NFPA defines a "Draft Curtain" as a “Fixed or Automatically deployable noncombustible barrier that protrudes downward from the ceiling to channel, contain or prevent the migration of smoke.”
Reply
Mohamed Hassan, CFPS, CFI I, PMP
5/9/2022 08:28:55 am
The guidelines for selecting the material of draft curtains are provided at NFPA 204.
Reply
Alex
5/9/2022 08:43:22 am
Hi,
Reply
Eric R
5/9/2022 09:41:14 am
When we install interstitial sprinklers, our jurisdiction uses the IBC so what Todd posted is what we are used to.
Reply
Patrick Drumm
5/31/2022 07:24:40 am
Apologies for the delay, but thank you everyone for submitting there comments. They were very helpful all around to confirm the acceptable materials.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |