What is the proper point in a system to take the antifreeze sample?
I have taken readings at both outlets at the check valve, unfortunately a contractor is saying to take it at the most remote point. Those locations are either 25-feet in the air, or not installed at all. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments
Dan Wilder
2/23/2023 08:14:36 am
You are both correct per NFPA 25 - 23' Edition
Reply
Todd E Wyatt
2/23/2023 09:20:49 am
A similar prescriptive requirement for the “test connection(s)” for “Antifreeze systems” is referenced in “2022 NFPA 13 — Standard for the Installation of Sprinkler Systems” which references “2020 NFPA 25 Standard for the Inspection, Testing, and Maintenance of Water-Based Fire Protection Systems.”
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |