Pressure Reducing Valve are commonly used to prevent excess pressure upon systems when supplies exceed the NFPA limit of 175 psi.
There has been much discussion regarding the 'application' of these valves when hydraulic calculations are being provided to the discharge of the PRV and determining the pressure margin available. Currently, we have been instructed to calculate the system back to the PRV, use the PRV's friction loss calculator to determine friction loss through the valve and subtract that from the outlet setting to establish outlet pressure. This is then used as the available pressure at the outlet; minus the demand and you're left with the margin. I'm not sure that I agree that the valves 'friction' loss need to be considered unless you are at a point where the PRV can no longer provide the set pressure (when the supply is unable to provide sufficient inlet pressure to overcome the internal friction loss). Are there any 'papers' written for direction or other sources anyone might recommend? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
10 Comments
FIREPE25
5/17/2019 10:22:54 am
We see these calculated incorrectly very often. You are absolutely correct about the friction loss. If the valve is set for 150PSI and you have 190PSI before the valve the friction loss will be built in. The only time the friction loss is needed is when the valve is wide open (assuming we are talking about pilot operated PRV). This gets a bit tricky if the valve is set for 150PSI and you have 155PSI before the valve. We use SprinkCAD and we calculate them using the following steps. This may be a bit confusing but i will do my best.
Reply
PETE
5/17/2019 10:41:07 am
The PRV will output an entirely new water supply curve based on it's friction loss curve. One way to consider the losses is to plot the new water supply points based on the inlet water supply adjusted for friction loss at various points, and input that as your water supply. The other way is to add a set friction loss at your flow for each calculation. Either way is acceptable, but you can't just ignore it. The PRV will have friction loss even when the supply pressure is lower than the outlet pressure setting. Look at p.11 of this Cla-Val PRV. https://www.cla-val.com/documents/Technical%20Manuals/TM-90-21.pdf
Reply
FIREPE25
5/17/2019 10:52:38 am
I think I agree! In most instance the pressure after a pilot operated PRV will be a flat curve at whatever the set point is until the flow gets so large that the water pressure deteriorates to less than what the valve is set at.
Reply
M Akram M Ibrahim
6/20/2020 01:33:45 pm
Yes,if we see curve of inlet verses outlet pressure setting .though globe valve pressure drop is not more than 10 psi
Clifford Schulze
5/17/2019 04:20:44 pm
Be very careful when using the 2 1/2" brass pressure regulating valves. The pressure loss across those, especially at the higher flows, is substantial.
Reply
Nimal Tissa Wijetunga
5/18/2019 12:42:12 pm
PRVs are highly susceptible to failure and high maintenance requirements and therefore not recommended to utilize in Fire Protection Systems due to reliability considerations.
Reply
PETE
5/18/2019 02:23:59 pm
^^Citation needed. There are UL listed and FM approved PRVs on the market. Backflow preventers are high maintenance also, but they're required in some jurisfictions invariably.
Reply
Mike
5/19/2019 01:22:47 am
When installed correctly and maintained per NFPA 25, these valves are highly reliable. Most often if they fail, they were set incorrectly or not maintained.
Reply
Mike
5/19/2019 01:30:17 am
I think the delineation needs to be made between a pressure reducing valve and pressure regulating valve.
Reply
Serch
6/15/2023 04:33:40 pm
What about if I have a high pressure line for the top levels and a low pressure line with a PRV for the lower leves? I have a lot of doubts about how to run a calculaton
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |