Can a commercial pool be used as the required secondary water supply to a high-rise sprinkler system?
The 2019 IBC/CBC Section 403.3.3 requires an automatic secondary water supply in certain seismic design categories. This is typically met by installing a dedicated tank that meets the minimum demand for 30 minutes. I have a developer asking if they can run a feed line to their 100k +/- gallon commercial pool so it can serve this purpose. Outside of the engineering challenges and value engineering their team must address, I'm wondering if this arrangement is even allowed. I cannot find anything in IBC/CBC, NFPA 24, NFPA 13, etc. that wouldn't allow this. Any help is appreciated.
6 Comments
Mike L
12/28/2021 08:11:05 am
This was a question about a year ago...here is the link to the responses:
Reply
Jack G
12/28/2021 08:11:27 am
I ve done this before for schools, problem being vortex plate, and recovery. Of the 489:high rises I ve installed, only 24 had secondary and tertiary tanks. And they were tanks, not pools.
Reply
Alex
12/28/2021 08:21:14 am
Hi,
Reply
Jesse
12/28/2021 10:44:05 am
I seem to remember a discussion about this a while back.
Reply
Jon Nisja
12/29/2021 06:51:37 pm
As an AHJ, I have allowed an indoor swimming pool as a water source twice and regretted it both times. First of all, you have a major corrosion issue with pool chemicals. Secondly, swimming pools are maintenance-intense and can be out of service for maintenance and repairs for extended periods of time. One case was a secondary school and they would drain the pool in the summer (2-3 months with no water in it).
Reply
sean
12/31/2021 06:19:26 pm
i think one issue you also have to consider is that the pool then has to be full for occupancy. you cant have the pool be down for maintenance or emptied for weather or any other considerations.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |