My project scenario: We have 2-hour fire-resistance-rated vertical chases than span multiple floors. These contain plumbing vent piping. All the penetrations are properly sealed.
Does the chase still need to be provided a sprinkler due to the vent piping? Or, am I permitted to omit sprinklers in accordance with NFPA 13 Section 8.15.1.2.14? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Glenn Berger
12/1/2022 08:30:19 am
Based upon information provided, sprinkler protection of the chase would not be required.
Reply
Todd E Wyatt
12/1/2022 09:04:28 am
The condition you described is a Vertical Opening (VO) and not a "chase." This VO is enclosed by a 2-Hour Shaft Enclosure (2SE) based on the number of stories the VO connects and/or the fire-resistance rating (FRR) of the floor construction being "penetrated".
Reply
Jesse
12/1/2022 01:07:09 pm
I think you can omit AS protection in this area.
Reply
Moderator
12/1/2022 01:57:05 pm
Previous edited post on behalf of Dan Wilder (sorry, we lack an edit button, but you're always welcome to email us for corrections and info@meyerfire.com):
Reply
Darwin
3/14/2023 09:52:39 pm
NFPA 13-2022: 9.2.1.16
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |