We have a high-rise building, with rated stair shafts. This project is under NFPA 101.
Under NFPA 101, Is is permissible to penetrate the wall of the stair enclosure (an exit enclosure) with duct that is not serving the staircase? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Ray Ramos
4/26/2021 08:11:30 am
What we have done (at my current firm in NYC) is we provide a rated enclosure for the ductwork (2x gypsum boards back to back for the 2 hour enclosure) so that the ductwork is a "shaft" now and not within the staircase. You have have to make sure with the Architects the egress path clearances are not affected..
Reply
DG
11/23/2022 10:27:19 am
Reply
Richard Mercer
4/26/2021 08:14:29 am
Does not appear to be permissible.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |