A Level 2 Aerosol is to be boxed and stored on pallets at 15 feet with a ceiling height of 26 feet. Which of the following sprinkler protection criteria is acceptable? a. Standard Spray (K-factor at least 8.0) Sprinklers; 0.30 gpm/sqft over 2,500 sqft b. ESFR upright K14.0, quick-response, 12 sprinklers at 50 psi c. ESFR pendent K16.8, quick response, 12 sprinklers at 35 psi d. ESFR pendent K22.4, standard response, 12 sprinklers at 25 psi Solution | Posted 09/05/18
9 Comments
FPE
9/4/2018 08:04:55 am
a. Standard Spray (K-factor at least 8.0) Sprinklers; 0.30 gpm/sqft over 2,500 sqft
Reply
KC
9/4/2018 08:47:26 am
C
Reply
rob
9/4/2018 09:35:05 am
Table 6.16.3 indicates that B, C & D are all correct, based on the 15' storage height with a maximum ceiling height of 30'
Reply
Colleen
9/4/2018 11:45:10 am
I agree that C and D are both acceptable per FPH 6-264, Table 6.16.3, but B specifies upright sprinklers, and the table has requirements for ESFR pendent sprinklers.
Reply
G
9/4/2018 12:39:49 pm
C
Reply
mhk
9/4/2018 07:19:22 pm
b. I found this in NFPA 30B table 6.4.2.7(b) since NFPA 13 says NFPA 30B to be referred.
Reply
Mark
9/5/2018 01:14:49 am
I agree with the table but it shows ESFR-pendent. I think the answer should be C.
Reply
MHK
9/5/2018 02:50:32 am
You are correct. I overlooked the type of sprinkler.
Pari
9/4/2018 11:27:58 pm
B, C or D are the right answer per Table 16.6.3 since this year NFPA 30 B is not included for the test
Reply