Inergen (IG-541) is being used for protection of several rooms which contain highly valuable historic documents. If the fire type is considered Class A and the design concentration of Inergen is provided, determine the clean agent-air mixture density. a. 1.15 kg/cu. m b. 1.25 kg/cu. m c. 1.28 kg/cu. m d. 1.44 kg/cu. m Solution | Posted 06/07/19
7 Comments
Ralph
6/6/2019 10:18:41 am
NFPA 2001-2015
Reply
MDS
6/6/2019 10:30:06 am
Also found in:
Reply
Ryan
6/6/2019 10:41:31 am
I agree with this, but since NFPA 2001 is not on the required material list, you can find this information in the following sections of the SFPE Handbook, 5th ed:
Reply
Amr
6/6/2019 03:57:43 pm
C. 1.28
Reply
DM
6/7/2019 05:39:43 am
D 1.43 kg/m3 as per SFPE P 1526
Reply
DM
6/7/2019 07:29:34 am
C) 1.28 kg/m3
Reply
Brenton
6/7/2019 05:50:32 am
C. 1.28 kg/m3
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |