What is a building owner's responsibility to provide sprinkler system plans and calculations to new tenants and/or inspectors?
Is there any responsibility to provide these? Code sections would be appreciated, thanks. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Matthew Mueller
4/22/2021 09:51:48 am
NFPA 25, 2020 Edt.:
Reply
jay
4/22/2021 02:58:52 pm
Unfortunately 4.3.4 rarely happens and when a building changes ownership these get thrown in the dumpster.
Reply
Matthew King
4/24/2021 08:19:09 am
There is no section of NFPA that directly addresses the owners responsibility to provide this information to tenants. That is typically contractual/defined in lease agreement. Some jurisdictions have more succinct local requirements. As cited in another response to your question, the owner is obligated to maintain as-built conditions, and changes for the life of the facility. Typically, owners dont do this well, rather the authority have jurisdiction maintains copies of approval drawings. Some alarm company's have either a physical box with alarm drawings at each panel or more lately, the drawings can be pulled up in the panel itself in more modern panels.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |